  • #22941

    Yes cat 5 is for data…. I have seen cases where cat 5 has been used to control valves because (as in my case) I happen to have a spool of direct bury cat 5
    POE spec is 48 volts so I know it can handle that much (no idea about amps).
    My run is only a few feet so voltage drop not really an issue.
    Anyone using Cat 5 in this manner? Does it work or am I being a lazy idiot for not running real sprinkler wire 🙂

    #27083

    Samer
    Keymaster

    Based on this thread it seems possible to use Cat5: https://groups.google.com/forum/m/#!topic/alt.home.repair/X4UV5YNlF-E

    But not recommended I don’t think (since max or worst case current can exceed the cable max)

    #27084

    wayner
    Member

    Until a few weeks ago I had two sprinkler controllers – one in my basement and one on the side of my pool cabana. I wanted to consolidate these into one web-enabled controller in my basement – unfortunately I bought an IrrigationCaddy before I learned about OSPi. I had a spare CAT-6 drop running from my basement to my pool Cabana so I used that to go from one of the old unused controllers to the leads on my new IrrigationCaddy. I hooked it up about two weeks ago and it seems to be working fine.

    My run is probably at least 100 feet – probably longer as I bought a 50 ft CAT-6 patch cable, cut it in the middle and connected one end to the COM, and Zones 4-8 of my new controller and plugged the RJ-45 into my main LAN drop panel in the basement. I connected the other end to zones 1-5 of my old controller and plugged it into my LAN drop in the pool cabana.

Viewing 3 posts - 1 through 3 (of 3 total)