OpenSprinkler › Forums › Hardware Questions › DIY Kit Assembly Questions › Troubleshooting lower voltage on 1 station › Re: Re: Troubleshooting lower voltage on 1 station
June 3, 2014 at 6:08 am
#23236
Anonymous
Inactive
Opensprinkler v1.4u.
The PTC fuse next to the power switch gets very hot. A station will run for about 10 to 15 minutes then the unit faults, usually with the LCD dimmed. Unplugging then powering returns the unit to previous operation.
Power Supply output- 24VAC, 750mA
VIN-GND 5V, Over range Ohms
VCC-GND 3.3V, Over range Ohms
Can cycle through stations- ~25V output, 0.18A on the active station.
Rainbird Valve #35006905
Seems like this load shouldn’t be a problem based on the previous posts. What should I check to trouble shoot?