  • #37214

    cvonk
    Participant

    I notice the CFCI in the Orbit 57095 timer box tripping every few days.  The only thing plugged into the CFCI is the transformer going to OpenSprinkler.  Even if there was a ground fault, it would be on the secondary circuit of this transformer.  Besides, it is very dry here.  The only think wet is near the sprinklers that are far from the GFCI.  My main thoughts go to the magnetic fields of the transfomer messing with the GFCI.  Any other thoughts?

    thanks
    /c

    #37230

    Ray
    Keymaster

    I don’t have enough knowledge about GFCI. But I did some Google search and my understanding is that it trips when the difference between the supplied current and returned current is more than, say 6mA. This is often due to leakage current, unexpected shorting to ground, or anything that causes the current to leak out without returning. I can’t think of an obvious reason for your case, but I suspect if there is a wire that is worn out or exposed, it can result in leakage which trips the GFCI.

    #37237

    mb42
    Participant

    I have also seen this symptom (GFCI tripping unexpectedly) when there is more than one GFCI outlet on the same circuit.

    #37241

    cvonk
    Participant

    Thx.  The leak would be on the secondary winding.  This has been a while for me, but I don’t think something on the secondary can trip a GFCI.  The only other pointers that I can find hint at transient voltage, or ground connected to neutral.  I will check the latter when it is light outside tomorrow.

    #37252

    Mike
    Participant

    If everything else checks out OK, it could be a bad GFCI outlet.

    #37254

    cvonk
    Participant

    I found that the hot/neutral were reversed at the panel. The GFCI from the Orbit box  should have locked-out on this condition.  Oh well, I should have started with the 3 light tester anyway.  Condition corrected.  Will post the results in a few days.

    thx all
    /c

    #37698

    cvonk
    Participant

    Update: correcting the hot/neutral did the trick. OS is staying up and running, no longer hindered by the GFCI.

    /c

    #37776

    Ray
    Keymaster

    OK, thanks for the update. Useful tip in case others encounter the same issue.

    #39876

    tom
    Participant

    I was having the same symptom with my Orbit box, and discovered the same wiring problem. I presume its fixed now. thanks for the tip.