    cashperkins
    Participant

    has anyone use open sprinkler to control their landscape lights?  I have a 600w power transformer for my Malibu landscape lights right next to my open sprinkler box.  I would love to have the open sprinkler control times for the lighting. Is there something I could by that would enable me to do that?

     

    thx

    #37199

    brucep
    Participant

    Hi,

    Yes, I have a dedicated OS to control garden lighting, and some zones on my other 2 are also used to control lighting. All you need is a 24V AC relay per individual zone, which you connect in exactly the same way as a water solenoid, there are some details here: https://opensprinkler.com/using-24v-ac-relays-with-opensprinkler/

    Make sure you choose a relay with enough current rating to switch the entire load……if you have 600W transformer @12V that’s up to 50 Amps !!!

    Or break up the lighting into zones so you can use smaller relays, or even convert halogen into LED to reduce power consumption.