renoirMember@Archades wrote:
I will probably be using 7 core 0.5mm2 wire with them as well, would that be sufficient for running 24vAC 0.2amp running, 0.34amp inrush solenoids? 2 of them will be around 30meters from the OSPi so I’m not sure if that wire is thick enough to handle that current without too much voltage drop.
To keep voltage drop below 3% at 24VAC, 0.34 amps, cosphi 0.8 and a wire length of 30m, the wire cross-section needs to be at least 0.4mm^2. You’re good.
May 5, 2014 at 11:06 pm in reply to: sprinklers_pi – An alternative sprinkler control program #25088
renoirMemberHi Richard,
thank you so much for sprinklers_pi! This software is fantastic! Especially the automatic timer adjustment based on values provided by wunderground is a huge improvement over common on/off rain sensors. I’m interested a lot in this part of your program. So far I’ve found the formula in weather.cpp, however I don’t understand how this formula has been put together. If you could share your insights… I’m asking because slight modifications or even 2 distinct formulas might be useful. I use a micro irrigation system in my garden. My potted plants are on different circuits than those planted directly into the soil. Soil in pots tends to dry out faster (less volume, the pots are porous, etc), therefore I believe it would make sense in a fully automated irrigation system to take into account at least two formulas for different evaporation factors, one that kicks in sooner than the other. If you would comment on the formula, I’d have something to work with.
Btw, I already made a french translation of the webif and I could make a german one, too. If this is of any use, let me know where tho send the translated content.
-
AuthorPosts