  • in reply to: Zone’s won’t turn off #26387

    Wavy
    Member

    Figured it out… I had grabbed a 24VDC transformer. Replaced it with a AC transformed and everything is good.

    in reply to: Zone’s won’t turn off #26386

    Wavy
    Member

    I believe they are standard AC valves. I honestly haven’t ever paid much attention. When one would fail, I would just replace it with a generate one from Home Depot. Should I have been seeing 24VAC on the outputs of the OSPI rather than -24VDC?