    I have had my controller for almost 2 years and now I have a problem where the controller is pulsing a valve approx. every 5 sec for less than a sec.
    This occurs when the controller is powered but not “running” (i.e. rain delay, manual, etc).
    I have not updated the firmware or anything, it just started on it’s own.
    Has anyone ever seen this and might know the solution?

    Thank you for any help you can give me,
    Ryuser

    #37629

    pls90
    Participant

    I have a similar problem, but only when the valve is turned on.
    See http://opensprinkler.com/?post_type=topic&p=37355#post-37513

    #37754

    Ray
    Keymaster

    I honestly have not seen anything like this before. Can you try the following experiment: unplug the COM terminal block, restart the controller and wait for it to finish booting, then plug in the COM terminal block. Does it still pulse? If so, this is either an issue with the shift register or triac; if not, this is an issue with sprinkler solenoid. Let me know what you find out.