OpenSprinkler Forums Hardware Questions OpenSprinkler Pi (OSPi) Debugging intermittent valve failure

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #49933

    bburan
    Participant

    My OpenSprinkler Pi has been working nicely for two years with a two-zone system. Last weekend I installed four additional zones for a total of six zones. I tested all valves and they were working fine. However, a day or two later the valves stopped opening when I attempted to activate them via the web UI. When I grabbed a multimeter and measured the voltages at the OpenSprinkler Pi terminals, they were responding as expected. Strangely enough, the valves started working again without me doing anything else.

    However, this morning they stopped responding again. What should I do to debug this problem? My guess is that it’s either a power supply, Open Sprinkler Pi or ground wire issue (since all or none of the valves work). Any suggestions for the first few things I should look at?

    #50052

    Ray
    Keymaster

    Maybe check if there is any wiring issue. A useful test is to check resistance: from COM to each zone port, measure resistance. Typically 24VAC sprinkler valves should have a resistance of somewhere between 20ohm to 50ohm. If it’s too small or too large, that indicates wiring or connection problem.