    Trying to set up a solid state 12v rf relay . The fob has only single buttons press once for on press again off. works fine. Is this possible to use with open sprinkler hardware v.3.2 DC and firmware 2.2.1(3)? I used the rf toy and recording on get H00000002——–01490105 which is 17 digits. Is this a problem? Also when entering code in advanced station setup should the dashes be included?. thanks for any help rwp

    #84129

    Ray
    Keymaster

    If the remote has one button, then the ON and OFF codes are the same. You should NOT include the dashes — OpenSprinkler firmware will only accept hex code, dashes are invalid. In your case, the complete code should be:
    H000000020000000201490105
    It’s a total of 25 characters.

Viewing 2 posts - 1 through 2 (of 2 total)
  • You must be logged in to reply to this topic.