    My two programs are setup to run 4 zones each for 20 minutes at 0400 repeating once after the whole run.
    Saving the programs is fine.
    Review Programs looks like they should run.
    They haven’t run.

    When I go to a program in Edit Programs and click Save Changes to {Program} (or even duplicate the settings manually and save) everything works fine.
    However, if I click Run {Program} from the Edit Programs page for a program, it pops the dialog “Please check input and try again.”

    Run-Once Program does run a partial equivalent of the program correctly (that is, it does the right thing but it doesn’t repeat).

    #61749

    Ray
    Keymaster

    The first thing to check is whether you have set the program to ‘Use Weather Adjustment’, because that means the run time will be affected by the watering percentage. If your watering percentage is small or 0%, that will prevent the program from running.

    The other thing to check is whether you’ve set your location correctly, so that your time zone and time are correct. If not, the program will run at a different time than you anticipate.