I have a B Model BBB connected to the local internet by ethernet cable . I am running twelve valves on individual programs in sequence. Manually the valves will turn on using either the manual on page or the program page. The clock is running with the correct time. The timeline travels down the programs but they don’t turn on. I need your suggestions?
Walter Loehnert
Check to see if the controller is left in ‘manual mode’. When it’s in manual mode, the normal programs will stop running. You should click on ‘Manual Off’ button (at the bottom of the homepage) to set it back to program mode.
Thank you Ray for your answer, this solved my problem. Looking forward to using weather station information. Thanks for the greeat product.