October 8, 2016 at 12:08 pm #44292
os-fanParticipantWhich component on the expansion board going bad would account for the following symptom on one zone?
+24 VAC is present on zone when not connected to sprinkler solenoid, however voltage drops to 0 as soon as connection is made.
Connected this sprinkler solenoid to a different zone and it works as it should – solenoid turns on.
Sent from my iPad using Tapatalk
October 10, 2016 at 4:17 am #44297
AugustinParticipantConnected this sprinkler solenoid to a different zone and it works as it should – solenoid turns on.
When you did the test with a different zone, you used same wires from the solenoid to the controller?
If answer yes: I don’t have enough knowledge to answer.
If answer no: The wires between controller to solenoid are shot, I had a similar case and I tested like you did but I tested also the wires and turn out to be the wires I had to re-route.October 10, 2016 at 8:51 am #44302
os-fanParticipantWhen you did the test with a different zone, you used same wires from the solenoid to the controller?
Yes, I just moved the wire from the bad zone to a different zone. The solenoid is 150 feet away in a sprinkler box, so I don’t think it’s the wires or the solenoid itself. After removing the wire from the bad zone, that’s also when I noticed that the +24VDC was present, but that it would drop to 0 as soon as I re-connected the wire.
October 11, 2016 at 2:44 am #44314
RayKeymasterJust to double check, when you say you measured 24VAC, did you measure it from the common (COM) wire to that zone, or some other points? The correct way is to measure between common wire and that zone. I really can’t explain what you are observing: if the voltage between common and that zone wire is 0, either there is a shorting on the wires (or the solenoid is shorted), or the triac switch is damaged open (essentially leaving the circuit open). However, the fact that you can measure 24VAC without connecting the zone wire means the triac switch should be working.
There is a way to directly test the triac. Specifically, use the multimeter’s diode testing functionality to measure the diode forward drop voltage between gate and T1 pin (red probe on gate, and black probe on T1). You can find the pin layout on the datasheet:
http://www.ween-semi.com/documents/BT1308W-400D.pdf
page 3 (note that gate is marked 3 and T1 is marked 1). If the triac is ok, the forward drop voltage should be about 0.6 to 0.7V. Otherwise the triac is damaged.October 12, 2016 at 10:11 am #44322
os-fanParticipantRay, I am measuring voltage between the common wire and this wire. I’ll check the triac this weekend and let you know. There is no real urgency because the sprinkler is currently working on a different zone, but I am curious to understand what is going on.
Sent from my iPad using Tapatalk
January 19, 2017 at 11:53 pm #45234
Bowman ModParticipantSame problem here with 24vac present on station 05. No current capability. Solenoid or wire is not the fault as I’ve moved the wire to station 06 and works fine. Has been no storms or power spikes that I’m aware of.
Hardware issue?
January 22, 2017 at 11:32 pm #45281
RayKeymasterI suppose it’s possible that the triac os that station is damaged, so even though there is voltage, the triac is not capable to sink any current through it. You can check my post above (#44314) for diagnosis instructions, or you can submit a support ticket and ship it back to us so we can check it for you.
May 19, 2017 at 5:11 pm #46304
alexjensentxParticipantI’m reporting the same problem on my end. Station 4 (24 vac) delivering no current. Moved the wire over to Station 6, and its working correctly. Definitely a hardware issue. Any warranty coverage on this?
May 20, 2017 at 6:49 pm #46323
Bowman ModParticipantAlexjensentx. Message support directly, Ray may be able to help you out.
I wonder if this hardware issue was fixed on the quietly released hardware 3.0?
May 21, 2017 at 3:59 pm #46368
RayKeymasterAlexjensentx: please send a support ticket about the issue.
OpenSprinkler 3.0 uses exactly the same driver circuit as previous versions. The only change is the microcontroller (from ATmega1284 to ESP8266) and the size of the controller.
-