  • #22572

    ndboost
    Participant

    a power outage occurs and the sprinkler system has a zone on?
    the rpi freezes and a sprinkler system has a zone on?

    Is there a failsafe built in to the board/shift register?

    #25179

    mattguy
    Member

    Well if the power goes out, I’m figuring that you don’t have a backup power supply just for your sprinkler system, so the sprinklers should also turn off since there isn’t any power being supplied to the solenoids. Now when the power comes back on, the sprinklers should stay off since the opensprinkler Pi needs a command from the pi board to turn the solenoids on which would allow the water to flow. I’m nearly positive this is how it would work, but don’t take my word for it 😛

    #25180

    ndboost
    Participant

    Im going to have to do some actual testing of both of these scenarios i fear.

    #25181

    Ray
    Keymaster

    First, if power goes out, the sprinkler valves are clearly deactivated, because the valves run on 24VAC from power adapter, they don’t run on batteries.

    Next, if RPi freezes, it can indeed leave a valve on. There isn’t a watchdog timer on the OSPi to handle this potential issue. But frankly I don’t know how often RPi freezes. I’ve never encountered this myself.

    #25182

    ndboost
    Participant

    Its a rare occasion indeed. Good to know though thanks Ray.